Quote from: S.Yu on April 12, 2021, 00:27:59
Drain the liquid before opening the lid, even I could think of that.
A tank is going to contain several servers. In this case, I believe there are about 40 blades. Draining the tank would mean you have to shut down all of them first. That's not what you want. That's like shutting down a whole rack to work on a single server. And in that case, simply switching them off should rapidly reduce evaporation in itself. Or just removing load from them. A server can take very long to start up (I have seen servers that take over half an hour). Frankly, it might be better to just leave it be and allow problems to accumulate.
I recall that 3M demonstrator from 2012 reportedly had very small losses from hot-swapping. I don't think they quantified it. They also claimed servers can be pulled out dry. In their case, the heat exchanger was mounted well bellow the lid, off to the side. And the whole thing was operating at atmospheric pressure. There should have been a layer of air beneath the lid. Also, they mentioned they had an extra heat exchanger just for hot-swapping. It was mounted above the primary, close to the lid I believe.
I did design an immersion cooling solution over 10 years ago. But I was primarily concerned about creating a front-loading system rather than a top-loading bath. It seemed like an interesting challenge given that liquids will pool down due to gravity. Horizontal baths struggle to utilize vertical space which is typically abundant in datacentres. Not that lifting heavy servers up is fun.